A 3-phase induction motor draws 1,000 kVA at a pf of 0.8 lag. A synchronous condenser is connected in parallel to draw an additional 750 kVA at a power factor of 0.6 lead. The pf of the total load supplied by the mains is | |
A. | unity. [Correct Answer] |
B. | 0.707 lead. [Wrong Answer] |
C. | 0.6 lag. [Wrong Answer] |
D. | zero. [Wrong Answer] |