Two 10 kV/440 V 1-phase transformers of ratings 600 kVA and 350 kVA are connected in parallel to share a load of 800 kVA. The reactances of the transformers, referred to secondary side are 0.0198 Ω and 0.0304 Ω respectively, (resistance negligible). The load shared by two transformers will be | |
A. | 484.5 kVA and 315.5 kVA. [Correct Answer] |
B. | 315.5 kVA and 484.5 kVA. [Wrong Answer] |
C. | 533 kVA and 267 kVA. [Wrong Answer] |
D. | 267 kVA and 533 kVA. [Wrong Answer] |